Re: POWER QUALITY SURVEY needed in San Francisco area.
Originally posted by awwt:
How do PQ testing companies calculate their pricing?
What are the procedures?
What about EMF testing pricing?
What are the procedures? What is the workflow for the testing company?
They determine the price by the size of the distribution system, complexity, and to what level of detail you are looking for. For example, they are generally in three categories:
Level 1 Survey. Testing and analysis of the AC distribution and grounding.
Level 2 Survey. Level 1 plus monitoring ac voltage supplying the equipment over a given time.
Level 3 Survey. Levels 1 and 3 plus environmental monitoring over a given period of time.
Before you jump in you need to establish some parameters such as:
What equipment is having problems.
Types of malfunctions (data loss, lock ups, component damage).
When do problems occur.
Existing protection for equipment.
Possible problem sources. (elevators, HVAC, copy machines)
Coincident problems occurring at the same time. (lights flicker, motors slow down)
You will need to collect all equipment manuals, have a staff electrician available, and get the utility involved.
How much you say. Hard to answer, but you can bet several thousand for a large facility. So you need to justify the expense by looking at how much money has been lost by equipment damage, data loss, production downtime, etc. If all you are talking about is light bulbs and a couple of copiers in an office environment, good luck. I would charge $1500 per day on site plus expenses and detailed written report.