cadpoint

Senior Member
Location
Durham, NC
Occupation
Electrician - but not by NC Law.
I was just pondering if one was to take a voltage reading at service point or to say branch service, or any service and note that there seems to be
a higher or lower than expected, Voltage.
I've watched my house for years and always note conditions on jobs and the reading obtained locally, they frankly all are riding a little higher!Thoughts ?
 
I see
277= 281
120= 124
208=211
more often than not around here. This is at main disco's under load. Often I find 1 phase to be dead nuts and the other 2 slightly high.
 
Most utilities have a range of voltages plus or minus nominal according to their state's public utility commission. The utility I work for goes by ANSI C84.1 which says for Range A, which is steady state range, the voltage should be +/- 5% of nominal.

So my answer is 114 to 126 V for a 120 V base.:)

There is also range B for short duration variances outside Range A.
 
You should expect 5-10% below nominal at around 4AM, then steady increase until peak at around 3PM where it reaches 5-10% above nominal, starts to taper off, big drop around 5PM, another drop around 10PM, and low values from 1AM to 4AM
 
No load xformer voltage high if the little red light is on in the hood that means overload and the volts will be low unless they bumped up the taps.
 
than expected, Voltage

I never expect to see anything, I test the service/conductors, phase to neutral, phase to ground and phase to phase. I make any Power Quality determinations base on this and amperage readings.
 
You should expect 5-10% below nominal at around 4AM, then steady increase until peak at around 3PM where it reaches 5-10% above nominal, starts to taper off, big drop around 5PM, another drop around 10PM, and low values from 1AM to 4AM
 
Some utilities allow +- 10%, so most devices are built to that as a standard voltage tolerance. +- 10 volts on a 240V (<5%) system is not a problem. If you measure that at a 120V connection, its possibly a little high, but still not likely a problem for your equipment.
 
Typically when monitoring the main I see highest usage at 11:30-1:30 When elevators, HVAC and office loads are on same source/service.

30 Day voltage graph.

VOLTAGE1.jpg


11 day (same project) current graph average.

Voltage2.jpg


One day Monday, red is from 7:55 AM through 6:40 PM, purple line is 5:00 PM-6:00 PM

VOLTAGE3.jpg
 
At the facility I work at, we were seeing 500v on a 480v nominal service. That's not that far out there, but we reported it to our POCO and they took a few caps off line at the local sub-station. That brought the voltage back to just over 480V.
 