Something has always confused me. When you look at the nameplate of a range, it gives a kilowatt rating for 208v and a kilowatt rating for 240v. Like almost any other appliance in existence, it might be tempting to figure out how much power is required by looking at the nameplate. In this case, take 9100 watts and divide by 208v and you get 43, which I would figure means the thing uses about 43A max, so I would run a 50a circuit. Take 12100 watts and divide by 240 and you get a different figure, just over 50. That alone has confused me already, there is no three-phase connection so why would 240v draw a larger amperage? At any rate, this is a low-cost GE range and it says in the instructions to put it on a 40a breaker. Fine.
Here's the thing though, not all range instructions tell you what size breaker to put it on. You can pour through the installation instructions and won't be able to find it. Today I looked at another GE range with an induction cooktop. It never says anywhere what breaker to protect it at or to supply the range with, (we looked hard), it only says "use a 40a rated cord". Well, I guess if the cord is rated at 40a, then you can put it on a 40a breaker. GE is a nice brand though, they tell you what to use, some brands don't. At any rate, I don't know why they put a name plate on that always is larger than 40A.
In the end, I don't care, no one is going to put all their burners on high and turn the oven on to 500 degrees. Still, it would be nice to know what to install it at. Frankly you can't go wrong with 50a in this case, but some ranges have higher nameplate ratings, what then?

Here's the thing though, not all range instructions tell you what size breaker to put it on. You can pour through the installation instructions and won't be able to find it. Today I looked at another GE range with an induction cooktop. It never says anywhere what breaker to protect it at or to supply the range with, (we looked hard), it only says "use a 40a rated cord". Well, I guess if the cord is rated at 40a, then you can put it on a 40a breaker. GE is a nice brand though, they tell you what to use, some brands don't. At any rate, I don't know why they put a name plate on that always is larger than 40A.
In the end, I don't care, no one is going to put all their burners on high and turn the oven on to 500 degrees. Still, it would be nice to know what to install it at. Frankly you can't go wrong with 50a in this case, but some ranges have higher nameplate ratings, what then?