Power strip inside operating room

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Can power strip with hospital grade outlets be used inside operating rooms and not violate any codes?
 
517.19(C) states “Each operating room shall be provided with a minimum of 36 receptacles divided between at least 2 branch circuits....”
 
The NEC is mainly for premise wiring, not for utilization equipmen. I don't recall seeing any info on portable power taps,. Check with your hospital accreditation agency.
 
The NEC is mainly for premise wiring, not for utilization equipmen. I don't recall seeing any info on portable power taps,. Check with your hospital accreditation agency.
^^^^^^Very much this. In NJ it's the Joint Commission, and they can and do go beyond the adopted codes.
 