I am having a difficult time understanding section 725.41
What this section seems to imply is that I could use class 2 cables and a class 3 power supply, which in my opinion is not safe.
Does this section confuse anyone else? I still think you must have class 3 cable if you are using a class 3 power supply, not class 2 calbe and a class 3 power supply.
Any thoughts?
Thanks,
I always figured you could supply a class 3 circuit with a class 2 power supply (and call it a class 2 circuit), but I don't think you can supply a class 2 circuit with a class 3 power supply. Class 3 circuits are considered to be safe from a fire perspective, but not from an electric shock perspective. Class 2 circuits, however, are safe from both.725.41 Power Sources for Class 2 and Class 3 Circuits.
(A) Power Source. The power source for a Class 2 or a Class 3 circuit shall be as specified in 725.41(A)(1), (A)(2), (A)(3), (A)(4), or (A)(5):
(1) A listed Class 2 or Class 3 transformer
(2) A listed Class 2 or Class 3 power supply
(3) Other listed equipment marked to identify the Class 2 or Class 3 power source
Exception No. 1: Thermocouples shall not require listing as a Class 2 power source.
Exception No. 2: Limited power circuits of listed equipment where these circuits have energy levels rated at or below the limits established in Chapter 9, Table 11(A) and Table 11(B).
(4) Listed information technology (computer) equipment limited power circuits.
FPN: One way to determine applicable requirements for listing of information technology (computer) equipment is to refer to UL 1950-1995, Standard for Safety of Information Technology Equipment, Including Electrical Business Equipment. Typically such circuits are used to interconnect information technology equipment for the purpose of exchanging information (data).
(5) A dry cell battery shall be considered an inherently limited Class 2 power source, provided the voltage is 30 volts or less and the capacity is equal to or less than that available from series connected No. 6 carbon zinc cells.
Any thoughts?
Thanks,