Hey everyone,
I'm doing a power systems study for a data center and the substation transformer has two KVA ratings based on the cooling system being used. When using ambient air for cooling the transformer is rated at 750 kVA and has and impedance of 5.99%. When using forced air for cooling, the transformer has a rating of 1000 kVA. I'm assuming it would make sense to use the worst case scenario of 1000 kVA for my study, but does the impedance stay the same when using this higher kVA rating? The transformer nameplate only lists the impedance for the 750 kVA rating.
Best Regards
I'm doing a power systems study for a data center and the substation transformer has two KVA ratings based on the cooling system being used. When using ambient air for cooling the transformer is rated at 750 kVA and has and impedance of 5.99%. When using forced air for cooling, the transformer has a rating of 1000 kVA. I'm assuming it would make sense to use the worst case scenario of 1000 kVA for my study, but does the impedance stay the same when using this higher kVA rating? The transformer nameplate only lists the impedance for the 750 kVA rating.