I thought this was changed in 2020.You are not permitted to run two circuits to a second building. You will need a feeder and a panel at the second building. 22530.
Bonding to the steel structure might be required. You would need to carefully read article 250 to tell for sure. Might be easiest to just run the wire.Thanks for your Reply. Would you have to do any bonding to the steel structure if all you was installing is the 50A 240v outlet and a 120 volt outlet
That change applies only to feeders, not branch circuits. A new section in 225.30 "Common Supply Equipment".I thought this was changed in 2020.
This was added for the 2020, but still does not permit two branch circuits.I thought this was changed in 2020.
225.30(B) Common Supply Equipment.
Where feeder conductors originate in the same panelboard, switchboard, or other distribution equipment, and each feeder terminates in a single disconnecting means, not more than six feeders shall be permitted. Where more than one feeder is installed in accordance with this section, all feeder disconnects supplying the building or structure shall be grouped in the same location, and the requirements of 225.33 shall not apply. Each disconnect shall be marked to indicate the load served.
In my opinion, those are all the same voltage system for the application of 225.30(E). I would never see two circuits that originate from the same service equipment as being of different voltages unless there was an intervening transformer.That change applies only to feeders, not branch circuits. A new section in 225.30 "Common Supply Equipment".
Now, as one branch circuit would be 120/240V 3 wire, and the other would be 120V 2 wire, then does that qualify under (2017) 225.30(D) as "different voltages"?
If one circuit were 240V 2 wire and the other were 120V 2 wire, then I think it clearly would.
Cheers, Wayne
Certainly.In my opinion, those are all the same voltage system
And if 225.30(E) said "voltage system" instead of "voltage" I would agree with you. But it doesn't.for the application of 225.30(E).
Take it up with a higher authority as I am putting a red tag on the installation.Certainly.
And if 225.30(E) said "voltage system" instead of "voltage" I would agree with you. But it doesn't.
Cheers, Wayne
Same here.I would want a feeder and panel anyway.
Me too.Take it up with a higher authority as I am putting a red tag on the installation.
Whatever happened to "the NEC says what it says, not what you think it says"? (2020) NEC 225.30(E) lists "different voltages" as one of the criteria. 120V != 240V. Those are different voltages, end of analysis.Me too.
Yes, unless you can use the six-handle allowance.Is a main breaker required by code in the New panel.
See Part II of article 225.Is a main breaker required by code in the New panel.
I believe the panel you're thinking of, in the detached building, would be classified as a subpanel, and would not require a "main breaker," although having one might not be a bad idea. whether the subpanel is required or not (one feeder/branch circuit vs multiple feeders/branch circuits) is a different question.Is a main breaker required by code in the New panel.