I'm not sure if this is the right place for this question but here goes..
I am working with a transformer repairman on resistance issues with the secondary side of some 3phase transformers. We have had resistance readings that are greater than 5% between X12, X23, X13. After analysis if appears that the source of the problem was "loosely" torqued connections.
Here is one example:
Resistance found: X12=.003902, X23=.002968, X13=.004036
Torque found: X1=20,19 ; X2=22,21 ; X3=15,17
All LV connections (from coil to bushing) were torqued to specification (26 ft-lb). The unit then tested fine and resistances were X12=.003213, X23=.003171, X13=.003226.
So my question is.. How would the secondary resistance of a transformer be effected if torque on X1, X2, X3 were inconsistent from bushing to coil, or from phase to phase? The above example was inconsistent phase to phase and here is an example of one inconsistent from bushing to coil.
Resistance found: X12=.003402, X23=.002824, X13=.003420
Torque found X1=25,30 ; X2=27,30 ; X3=24,31
All LV bushing connections were torqued to 30 ft.lb to be consistent with the coil connections torques. The unit tested fine and resistances were X12=.003220, X23=.003167, X13=.003255. Would inconsistency in torque between the coil and bushing connections cause resistance from phase to phase to vary that much?
Thanks for any input,
David P. - QE
David P. - QE