Re: Powerfactor and cable
It's hard to type with my tongue held firmly between my teeth, errr, my fingers held in my teeth.
But I can't let it go. I can't say I agree with some of the statements on VFDs
To paraphrase a conversation with an AB rep:
Rep: "At 60Hz it's 95% efficiency and 95% pf."
My response: "So what you are saying is if I want to run at line frequency rpm I only have to pay for 105% power. Think about this for a minute, why would I care about the eff and pf at 60Hz? If I was going to run at 60 hz, I wouldn't need a VFD. I'm much more interested in the eff and pf at say 45 hz. So what is it at 45 Hz?
Rep: "Uhhhh ..."
It seems to me that if line freq rpm is fine, then soft start is best accomplished by using a ... drum roll ... Soft Start - say an AB SCR soft start.
And power factor correction is best accomplished by caps.
Before I get beat to death, please keep in mind I've rarely seen any need for soft starts or pf correction under 50 hp.
All of the cases where I have used VFDs, were rpm/torque application specific. PF correction/VAR correction were not the issue.
I can't imagine a VFD is cost effective for only
VAR/pf - especially since you get to throw away 5% of your power.
Question for bg concerning: "Reduced danger of transformer overheating and equipment damage associated with harmonics."
Reduced from what? A motor without a VFD doesn't have any. Caps don't introduce any. A soft start only does during the few seconds while it starts. This one eludes me.
VFDs are great devices - if you need one - otherwise its just a power and maintenance hog. And yes, generally speaking, a DIT preferably or input reactors are absolutely necessary or the VFD can introduce horrible notching on the power supply.
carl