Powering a motor from two separate disconnects
Yes, this is direct coupled to a rather large compressor. This is running off a VFD so the inrush is not as high as it would be starting across the line, but probably still too much for the 400A disconnect but not the 600A fuses somebody jammed into it. (See below) o_O
IIRC older FRS fuses used to have a longer barrel and wouldn't have had a chance of fitting in that 400 amp fuse holder without some modifications.
Yes, the older style had a longer barrel. If you notice, these are rejection type fuses with a potion of the lower blade notched out. Seeing these hanging down below the fuse clips should have been the second clue when the 'engineers' installed them. The first obvious clue would have been the 600A rating of the fuse vs the 400A rating of the disconnect. This still blows my mind.
Sound like you have some creative engineers not beholden to code.
You could plausibly use both circuits to run a single motor if there were some device which properly split power consumption between the two sources, eg some sort of dual input VFD.
I could imagine using a pair of active front end rectifiers feeding a common DC bus supplying the VFD which runs the motor.
I could also imagine that simply designing such a system would be more expensive than simply installing the proper circuit, unless a supplier actually has an existing design available off the shelf.
Jon
Your fuse holder isn't a rejection type fuse holder so even a non rejection fuse type in 400 amp size would plug into this.