Ray83
- Union city Ga USA
We have arc flash ratings labeled on our switch gears and one of them say 40.38 cal. Should we buy a 50 cal? And anything pass 40 cal ( even if it's that .38 ) is that pretty much a major kaboom ?
what i was told by the fellow who gave me my arc flash training
is that ppe levels above 40 calorie didn't accomplish much, as a
level much above 40 calorie will result in an explosion that will
kill you from the concussion.
I believe the 40cal/cm^2 clothing 'limit' is likely to be removed in the 2018 edition of NFPA70E.
I think at some point NFPA 70E is going to have to take practicality into account. I think NFPA is afraid of being sued so they are making it almost impossible to do anything.
An argument can likely be made that NFPA-70E wants to reduce, if not out right ban, energized work.
Agree. Really, the only live work that should be justifiable is IR scanning.
There is also some troubleshooting that requires energized equipment.
The great miracle of the United States is that anybody can sue anybody for anything. That's why NFPA includes this disclaimer:
"The NFPA disclaims liability for any personal injury, property or other damages of any nature whatsoever, whether special, indirect, consequential or compensatory, directly or indirectly resulting from the publication, use of, or reliance on NFPA Standards. The NFPA also makes no guaranty or warranty as to the accuracy or completeness of any information published herein."
Voluntary consensus standards (NFPA, ANSI, etc.) are one-size-fits-most "best practices," so they're conservative. Nothing stopping us from being more--or less--conservative, depending on specific circumstances.