- Massachusetts
300.34 Conductor Bending Radius.
300.34 does not apply here, that is for conductors operating over 600 volts
Futhermore - that type of box is available with the pig-tail pre-installed the right way - if you check with your supply house I'm sure they can locate and stock them.![]()
Back to the OPs question.
IMO no, what you have in your picture is a violation.
250.34(B)
I vote for a violation per 300.14. If the pig tail is bent around and through the back of the box it will be too short.
Ok I gotta say this. There are billions of metal boxes with bonding
screws installed inside the box. If you buy a box with a bonding screw
already installed by the manufacture it is inside the box. If you buy a box
that already has a bonding screw and pigtail installed by the manufacture
it's inside the box. I'm sure you've been doing this awhile and have
seen thousands of boxes with the bonding screw installed inside the box.
But, one day you think, "Wait a second here,This method of installing
the bonding screw inside the box,is all wrong, lookie-here it should be
installed on the outside of the box!" Then you post a picture of a box
with the bonding screw installed on the outside, on a NEC forum that
will be seen by hundreds of qualified ,highly trained electricians.
Like we are gonna say, "Sheer Genius!!! Why did'nt I think of that?"![]()
A typo? Generators.IMO no, what you have in your picture is a violation.
250.34(B)
300.15
". . . a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, pull point, unless otherwise permitted in 300.15(A) through (M).
All those methods (A through M) enclose or embed the connection point.
Sure.One could always use a longer piece of wire fr the EGC.
So far....I have yet to see one good reason to put the screw in the back of the box.
A typo? Generators.
I still think that a box "shall be installed at", and they don't just mean next to it
Yeah, but:It says what it says and no more, . . .
. . . at is not in.
Yeah, but:
300.15. "A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring."
I am pretty sure that the switch should be in the box.
Sorry that should have been 250.134(B)
You don't think there have been any good/code reasons posted yet?
The apprentice could install these much faster from the outside.
The most obvious "good" reason is a longer bit or a helper with no more than 1 thumb per hand.[/QUOTE]
They should be "opposable thumbs" also.
And get paid in monkeys.![]()
250.134(B) applies to the green wire in the MC or EMT. I have not moved that conductor.