In a class 1 div 2 lighting application. The light is rated for C1D2. Do you need a sealoff in this fixture or can you run GRC straight through the threaded hubs on the base of the fixture?
Check your fixture nameplate and OEM specs - many of the newer fixtures are internally sealed and do not require an external seal and would state that on the nameplate and specs if true for your fixture.