It can be done, however there are some concerns. First is climbing space. You will need to orient your risers so that you maintain climbing space.
Secondly, is there room on the pole for a set of primary terminations, and a set of transformers? While it is possible to do it, most utilities don't because of the clutter.
Theoretically it is possible, but practically, it usually isn't done without a driving need.