A adavey Senior Member Location New York Nov 3, 2006 #1 Where in the code is the minimum depth of a primary cable(s)(13.2kv) to be installed mentioned ??????????????
Where in the code is the minimum depth of a primary cable(s)(13.2kv) to be installed mentioned ??????????????
B bphgravity Senior Member Location Florida Nov 3, 2006 #2 Who owns it? If its for utilities - your answer is in the NESC If its privately owned, the answer is in Table 300.50 of the NEC.
Who owns it? If its for utilities - your answer is in the NESC If its privately owned, the answer is in Table 300.50 of the NEC.
J jtester Senior Member Location Las Cruces N.M. Nov 3, 2006 #3 Look at 300.50. Remember these are minimum's, and in general I would consider them inadequate. Jim T
A adavey Senior Member Location New York Nov 3, 2006 #4 I agree. The Rigid and PVC conduit depth seems inadequate. I've always spec'd 2'6" and was challanged by EC on my depth for direct burial. Thanks for the help.
I agree. The Rigid and PVC conduit depth seems inadequate. I've always spec'd 2'6" and was challanged by EC on my depth for direct burial. Thanks for the help.
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Nov 3, 2006 #5 See Table 300.50 minimum Cover 1 Requirements line 2.