Primary connection for 8320GY/4800 120/240V 1 PH Transformer

knorthouse

Member
Location
USA
Occupation
Automation
Hello All.

This is a question about the connection of the primary of an 8320GY/4800 120/240 1PH transformer. The transformer supplier has let us know that there only needs to be one conductor run from the Utility to the Transformer (Phase conductor). But I'm not sure then how a primary fault would be cleared if no EGC is also run. It's a fairly long run from the Utility to the new transformer location, so this is a concern. I'd appreciate any comments on this. Thank You.
 
Hello All.

This is a question about the connection of the primary of an 8320GY/4800 120/240 1PH transformer. The transformer supplier has let us know that there only needs to be one conductor run from the Utility to the Transformer (Phase conductor). But I'm not sure then how a primary fault would be cleared if no EGC is also run. It's a fairly long run from the Utility to the new transformer location, so this is a concern. I'd appreciate any comments on this. Thank You.
It’s actually two conductors in one cable, the center conductor is surrounded by a braided ground which is used as the return path.
 
Hello All.


IMG_6244.jpeg

This is a question about the connection of the primary of an 8320GY/4800 120/240 1PH transformer. The transformer supplier has let us know that there only needs to be one conductor run from the Utility to the Transformer (Phase conductor). But I'm not sure then how a primary fault would be cleared if no EGC is also run. It's a fairly long run from the Utility to the new transformer location, so this is a concern. I'd appreciate any comments on this. Thank You.
 
On top of the concentric neutral, the utility follows different rules.

They do not have a separate neutral and ground; the transformer gets the 4800V hot, the concentric neutral, and that's it.

-Jonathan
 