charlie
Senior Member
- Location
- Indianapolis
Re: Primary cut-outs
Don, I didn't catch Bennie's comment about SDS so I didn't address it.
Don, I didn't catch Bennie's comment about SDS so I didn't address it.
The only difference between load current and fault current is that the latter has "escaped" from it's intended path, and it's magnitude is determined by the impedance of that fault path.Load current is not a concern. Mitigating the effects of fault current, and the related voltage, is the problem.
Now at primary voltages Earth would be a conductor would it not? Even though you have a delta to delta isolation you would still have a Earth ground that would still be common between the two systems. so if the grounding at high voltages is common and you have a SDS system then why can't we have grounding be common at 240 volts and still have an SDS system?By Bennie: An ungrounded delta/delta is sometimes inserted to break the MGN current path.
The delta/delta makes the downstream system separately derived.