I am currently working on a project and am running into some issues I thought you could help me with.
There is a 13.2KV double ended loop on site with (3) sets of S&C unfused switches. The loop is composed 750kcmil conductors and fused on both sides. Therefore if a feeder burns out you can isolate it and replace it.
I wanted to tap one of the S&C switches (on the unswitched side) to feed a 2000KVA transformer. The xfmr is fused on the primary side (in the cabinet) and is about 600' away. I am also feeding it with 750's. The local inspector has raised a flag saying I violated code by not installing overcurrent protection right at the S&C switch. He is quoting 230-220. I am looking at 240.101 (B) which states you don't need overcurrent protection as long as the tap conductor is protected feeder over current device.
Any thoughts?
Thanks,
Tom Millard, P.E.
I am currently working on a project and am running into some issues I thought you could help me with.
There is a 13.2KV double ended loop on site with (3) sets of S&C unfused switches. The loop is composed 750kcmil conductors and fused on both sides. Therefore if a feeder burns out you can isolate it and replace it.
I wanted to tap one of the S&C switches (on the unswitched side) to feed a 2000KVA transformer. The xfmr is fused on the primary side (in the cabinet) and is about 600' away. I am also feeding it with 750's. The local inspector has raised a flag saying I violated code by not installing overcurrent protection right at the S&C switch. He is quoting 230-220. I am looking at 240.101 (B) which states you don't need overcurrent protection as long as the tap conductor is protected feeder over current device.