Can the feed to a primary side of a transformer be any length. I know there is a 25ft rule for secondary but if I wanted to feed a Transformer off a MPD panel is there any restriction on the Primary side feed for length?
 
Yes it can be any length. Any particular reason why you think that a limit to the length may be required?
When I used to work for a commercial outfit they would apply the tap rule even thought the wires were not tapped. So the total length between primary and secondary could only be 25ft. I always thought that was inaccurate but I did not have the final say in the matter. (Also just here to learn and get better so even when I am 95% sure of an answer I like to see what others have come across)
 
When I used to work for a commercial outfit they would apply the tap rule even thought the wires were not tapped. So the total length between primary and secondary could only be 25ft. I always thought that was inaccurate but I did not have the final say in the matter. (Also just here to learn and get better so even when I am 95% sure of an answer I like to see what others have come across)
Thanks for the clarification. In the field you'll hear many "code rules" (I'll call them electrical myths) that do not exist. It's always good to ask the questions.
 
The only thing I would add is the Art 450.14 about transformer disconnects. Obviously a lockable breaker works but it would need to include a location label or description on the transformer. When everything is within sight, you won't need the lockable or location description parts.
 
When I used to work for a commercial outfit they would apply the tap rule even thought the wires were not tapped. So the total length between primary and secondary could only be 25ft.
There is a tap rule like that, it's 240.21(B)(3) plus 240.21(C)(5). But that only applies if the conductors on the primary side of the transformers are a feeder tap. If they comply with the base requirement of 240.21 of being protected at their point of supply, the primary conductors do not have a length limit.

Cheers, Wayne
 