winnie
 - Springfield, MA, USA
 - Electric motor research
You calculated primary voltage divided by primary current. This gives the apparent input impedance of the loaded transformer.However i did the math and got 0.2 ohms for resistance
If this impedance was _only_ the transformer resistance, then your calculation would be correct. But most of the impedance is actually the magnetic field in the transformer core preventing the flow of primary current.
The _DC_ resistance of the transformer is a tiny fraction of the primary impedance. If the DC resistance of the transformer were the value you calculated, then all of the input power would be converted to heat in the resistance; just imagine how much power gets dissipated by 3000A and 0.2 ohm!
-Jonathan