Devin, is it be possible that the remaining process fluid within the Coriolis meter flex tubing (while no ACTUAL flow present) would create a false indication of SOME flow?
This is a correct premise as seen from one angle. " Hunting " is a known characteristic of an oversized control valve.Sounds like the valves are over sized. Proof of this is the fact that you lowered the inlet pressure and the control operation improved
yes, if it's not setup correctly it can do that. There may be some applications I'm not familiar with where that's typical but not in my limited experience. If it's a newer micro-motion, some models come with a free trial of smart meter verification you can run once as well, the first thing I would do is look at it compared to the other lines that are working as desired and what I suggested in the previous post. Someone may have mistakenly done a zero calibration during commissioning, should only do zero verification if it's a choice, factory zero is more accurate.Devin, is it be possible that the remaining process fluid within the Coriolis meter flex tubing (while no ACTUAL flow present) would create a false indication of SOME flow?