problem

Status
Not open for further replies.

jrannis

Senior Member
Ok i have a MCC that an engineer directed my company to feed a 120/208 3p 4 wire panel from. pulled the wire today and went to terminate and discovered that there is no neutral. Does anyone have any brilliant idea to make this work. Would a isolation transformer do it?

How about writing an RFI to the Engineer?
Maybe he should decide what to do.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
pulled the wire today and went to terminate and discovered that there is no neutral.
You mean you pulled the wire and then you "discovered" your own omission?

A 208D-to-208Y transformer sounds like the only way. Don't forget the GES.
 