It is difficult if not impossible to have certainty. You improve your odds by combining l-d-l with t-l-t where possible.
If you can have the equipment running when you open the disconnect you have a high level of confidence. Then follow up with l-d-l to confirm that you did not just interrupt the control circuit.![Smile :) :)](data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7)
If you are working on the motor side of a starter, for example, then you can be relatively confident if you open the a combined starter disconnect, or if you find no voltage at the input to the starter.
It seems to me that the toughest problem is to verify that your action was in fact what removed power if there are multiple controls and disconnects that affect the same equipment.
What is your suggestion?
Tapatalk!
If you can have the equipment running when you open the disconnect you have a high level of confidence. Then follow up with l-d-l to confirm that you did not just interrupt the control circuit.
If you are working on the motor side of a starter, for example, then you can be relatively confident if you open the a combined starter disconnect, or if you find no voltage at the input to the starter.
It seems to me that the toughest problem is to verify that your action was in fact what removed power if there are multiple controls and disconnects that affect the same equipment.
What is your suggestion?