Had an unusual trouble shooting call for unexplained breaker that began occasionally tripping after transition from generator power. The frequency of the trips began increasing from once every few months to weekly.
No intentional load changes and no obvious ground faults in the circuit. 225A thermal magnetic breaker replaced and tripping persisted.
Put current monitors on the circuit at the 75kVA 480Δ:208 transformer immediately downstream. With no load on the secondary we got an inrush of 2,300A. I've heard of inrush in the 15 range, but this was severe enough to actually cause cable slap in the conduits, which is definitely unusual for a transformer this small.
Further, for whatever reason the problem was suddenly so bad we couldn't even re-energize without tripping even after repeated attempts and the transformer was removed from service.
The voltages on this transformer were perfectly normal, no ground faults, and in the past once successfully energized there were no overload or overheating conditions.
What could cause a progressively worsening inrush current? I'm guessing some sort of failure within the iron, but I cannot explain it for the life of me.
Any theories?
No intentional load changes and no obvious ground faults in the circuit. 225A thermal magnetic breaker replaced and tripping persisted.
Put current monitors on the circuit at the 75kVA 480Δ:208 transformer immediately downstream. With no load on the secondary we got an inrush of 2,300A. I've heard of inrush in the 15 range, but this was severe enough to actually cause cable slap in the conduits, which is definitely unusual for a transformer this small.
Further, for whatever reason the problem was suddenly so bad we couldn't even re-energize without tripping even after repeated attempts and the transformer was removed from service.
The voltages on this transformer were perfectly normal, no ground faults, and in the past once successfully energized there were no overload or overheating conditions.
What could cause a progressively worsening inrush current? I'm guessing some sort of failure within the iron, but I cannot explain it for the life of me.
Any theories?