K8MHZ
- Electrician
The following is info that may help others in the future.
Complaint:
HO getting shocks, not static, from gas dryer (electric motor). It's plugged into a relatively new GFCI receptacle. GFCI never trips. The floor is tile.
The wiring has 'iffy' grounding. You may have a ground wire, but no actual ground. That's probably from scabbing from a 2 wire circuit with a three wire cable.
Test 1:
Place stainless steel bowl on dry floor near dryer. Measured 105 volts w/ high impedance meter from bowl to dryer door hinge.
At first, I suspected a fault in the dryer, but my instincts were leaning toward not.
Test 2: Run extension cord from GFCI receptacle into kitchen and check voltages from cord to water pipe. Found hot and neutral reversed.
Test 3: Found j-box w/ 3 three wire NMS cables. One old, two newer for the addition we were in. All the colors were connected right. There was even a ground wire there! No ground. Just a wire. Found that the old NMS was connected at the other end somewhere with black as neutral, white as hot.
Test 4: My Greenlee tick tracer is GREAT at locating hot vs. neutral if you know how to do it. I turned it on and it would indicate anywhere near the dryer. It would also indicate the proper hot wire. I was impressed.
The fix: Remarked and reversed the old NMS.
Verification: 1 volt from dish on floor to dryer hinge. Test at cord to H2O pipe showed correct polarity. Apprehensive HO No longer gets shocked, even barefoot. Tick tracer no longer indicates, even actually touching the dryer.
So, here is what I learned.
GFCI receptacles DO NOT prevent shocks. They may prevent bad ones, but not 'hefty' ones as the HO described.
My Greenlee tick tracer is the quickest way to check for hot/neutral rev. where there is no electrical ground close by. Much easier than dragging an extension cord to the nearest metal pipe or back to the service.
A stainless steel bowl makes a good test contact point and isn't as messy as water.
Complaint: