what is the calculation for getting the amp draw from a 35kw A/H
A/H air handler?what is the calculation for getting the amp draw from a 35kw A/H
what is the calculation for getting the amp draw from a 35kw A/H
3 phase
208
3 phase
208
wouldnt I just divide my kw by the voltage
I am having to design build with only a kw rating
Well, you are gonna need the MCA and MOCD info at some point and that is on the nameplate/spec sheet.
A lot of unit heaters only provide voltage and KW.
You need to calculate it in the feild.
Voltage, number of phases and power factor. Efficiency would be good too.A/H air handler?
most have a nameplate with required ckt ampacity and ckt protection
heater?
either way
need voltage and phase
A lot of unit heaters only provide voltage and KW.
You need to calculate it in the feild.
Are you referring to the various strip heat packages that may be available for a AHU?
If so yeah, those would be voltage and kW only.
I have just have never been told to size wire and breaker for a total unit (fan motor, dampers, heat, etc) and just given kW and volts.
Are you referring to the various strip heat packages that may be available for a AHU?
If so yeah, those would be voltage and kW only.
I have just have never been told to size wire and breaker for a total unit (fan motor, dampers, heat, etc) and just given kW and volts.
A unit heater is a stand alone heater with a small fan. The only rating given is the kw.
View attachment 16843
Kw in, heat out.Is that kW in or kW out?