I also use the greenlee 1810 for 1/2” Box offsets. Fast and no guessing. However it makes a 9/16” offset not a 1”. If I need to make a number of a different offset, I use an Evans offset bender.

http://evansbenders.com/
 
Sounds like it might be according to 340.116. How about you run rr from the panel through the basement to the lamp post, violation?

That is just a basic construction spec.

340.10(4) takes you to Parts II and III of 334.

334.10(3)
Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of ma- terial that has at least a 15-minute finish rating as iden- tified in listings of fire-rated assemblies.


Post light scenario is fine if basement is in dwelling unit.
 
That is just a basic construction spec.

340.10(4) takes you to Parts II and III of 334.

334.10(3)
Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of ma- terial that has at least a 15-minute finish rating as iden- tified in listings of fire-rated assemblies.


Post light scenario is fine if basement is in dwelling unit.
Thanks. I will follow that through.
 
Well, that's actually what the customer asked for, so perhaps it's for the best. I just loath EMT...

What sort of metal box is damp rated, or should I just use Bell boxes? (I'm assuming that a PVC box has the same bonding requirement as when using the MC cable...)

thanks.