When providing a disconnect for a chiller, is it sized according to the nameplate minimum ampacity or the max OCPD? For example, the min ampacity is 47.5, the max OCPD is 90. (It's a replacement unit. The existing wire is #6, the existing CB is 50A.)
60 amp disconnect, or 100?
Edit: I just looked it up before submitting this. It looks like I'm good with a 60A disconnect, according to 440.12(A)(1). I'll submit the question anyway, in case anyone has some thoughts on it. Maybe I'm missing something.