Roger, a minor correction which I think is relevant here: Its up to and including the service disconnecting means not service equipment. An OCPD after the service disconnect is still service equipment, but the GEC cant connect there.I think you may be confusing the EGC with the GEC? The GEC can bond to the grounded conductor anywhere before and up to the service equipment.
Roger
See the definition of Service Equipment in article 100, we can break it down into every item but the definition includes breakers, switches, fuses, so Service Equipment includes the disconnecting means.Roger, a minor correction which I think is relevant here: Its up to and including the service disconnecting means not service equipment. An OCPD after the service disconnect is still service equipment, but the GEC cant connect there.
I agree. My point however was that the GEC landing point is up to and including the service disconnect, not service equipment in general. Texie post #2 said to land in OCPD which I dont see how that is compliant (unless we are into the 2020 outside firefighter disco).See the definition of Service Equipment in article 100, we can break it down into every item but the definition includes breakers, switches, fuses, so Service Equipment includes the disconnecting means.
Roger
It can land at the weatherhead, the meter base, the unfused disconnect or he main disconnect panel. All of that, IMO is service equipment
The part you're missing is that the service disconnecting means is part of the service equipment.Apparently no one is listening to what I am saying or looking at the actual wording. 250.24(A)(1) does NOT say "service equipment" it says "...to which the grounded service conductor is connected at the service disconnecting means "
I am not disputing that, what I am saying is the GEC cannot land anywhere PAST the service disconnect, such as an OCPD enclosure, even though an OCPD enclosure is still "service equipment".The part you're missing is that the service disconnecting means is part of the service equipment.
Roger
I agree with that statement, which is service equipment.I am not disputing that, what I am saying is the GEC cannot land anywhere PAST the service disconnect,
Do you agree with this statement (assuming the service disconnect is a disconnect without OCPD)?I agree with that statement, which is service equipment.
Roger
Yes, which falls inline with the article 100 definition of service equipment which includes "switch(es)"Do you agree with this statement (assuming the service disconnect is a disconnect without OCPD)?
"the GEC cannot land anywhere PAST the service disconnect, such as an OCPD enclosure, even though an OCPD enclosure is still "service
equipment".
But a meter disconnect is listed in 230.82. A transfer switch is not, so it is different. The only way it is permitted is if it is the service disconnect.In my view the transfer switch in this installation is no different that a meter disconnect. Nobody ever claimed a meter disconnect was the service disconnecting means even before the code was changed that said specifically that it was not.
We had meter disconnects for decades and nobody ever claimed they were the service disconnect even before the code recognized them and said they are not service disconnects.But a meter disconnect is listed in 230.82. A transfer switch is not, so it is different. The only way it is permitted is if it is the service disconnect.
Ok I guess we are moving away from the NEC and into the "we've always done it that way and never been called on it" type of arguments......We had meter disconnects for decades and nobody ever claimed they were the service disconnect even before the code recognized them and said they are not service disconnects.