jxofaltrds
Inspector Mike®
- Location
- Mike P. Columbus Ohio
- Occupation
- ESI, PI, RBO
Its 240, not 120/240.
Are we talking about the same thing? Note 14-30R
From: http://www.whirlpool.com/digitalassets/LER3622PQ/Use and Care_EN.pdf

Its 240, not 120/240.
Are we talking about the same thing? Note 14-30R
From: http://www.whirlpool.com/digitalassets/LER3622PQ/Use and Care_EN.pdf
View attachment 9777
Since this appliance was designed for straight 220, I doubt that it had such a jumper. That is the root of the problem.
Most likely in its native environment one of the 220 leads was a grounded conductor.
Tapatalk!
Maybe it has a timer that uses 220 and needs no neutral, only 2 hots and a ground
The dryer is an import, but approved for North American use. 60Hz 208-240. The original install is from the 70s with 10/3 NM and a NEMA 10-30. However, Im thinking the correct outlet for this would be a NEMA 6-30r, which is on all A/C and fast food equipment rated 208/240.
If this weren't a dwelling unit then 250.119(B)(1) would permit removing the insulation to make an EGC.
Rob you got me thinking. Still not allowed in ANY retro/change/remodel application.
(B) Multiconductor Cable. Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, one or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length
When installing a 240 volt dryer, would you reuse the existing 10-30r or change it to the technically correct 6-30r?
I'm with you, this should have a NEMA 6-30 cord cap and recep. if this is in fact straight 240 and not 120/240. 2 ungrounded and equipment ground. Any other would be a violation in my view.
That's what Im thinking. Only issue would be re-identifying the white. But keeping it would be a bigger violation the other way around.
I will take tape over stripping in case this does get changed again years from now.
Good point.
maybe just slide off the insulation and leave it in the box.
The dryer already arrived, its straight 240, the label has no slash rating. Instructions call for 2 hots and a ground (though they are vague), however the plug is a NEMA 10-30r which means its 2 hots and a neutral, there is no ground.
I decided to just tape it and transfer the white to the ground bar from neutral bar. Had it been coming from the service I would just have left it but Id rather the panel remain a 4 wire feed![]()
I didn't read this before my above post.
Now you have made it worse. You are connecting what is probably labeled "N" in the oven to an equipment grounding bar in a 'sub' panel?
250.140 Frames of Ranges and Clothes Dryers. Frames
of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes
that are part of the circuit for these appliances shall be
connected to the equipment grounding conductor in the
manner specified by 250.134 or 250.138.
250.138 Cord-and-Plug-Connected Equipment. Non?
current-carrying metal parts of cord-and-plug-connected
equipment, if grounded, shall be connected to an equipment
grounding conductor by one of the methods in 250.138(A)
or (B).
(B) By Means of a Separate Flexible Wire or Strap. By
means of a separate flexible wire or strap, insulated or bare,
connected to an equipment grounding conductor, and protected
as well as practicable against physical damage,
where part of equipment.
I didn't read this before my above post.
Now you have made it worse. You are connecting what is probably labeled "N" in the oven to an equipment grounding bar in a 'sub' panel?
...