Proper seal off location

Status
Not open for further replies.

Harold Jacobs

Member
Location
Florida
Occupation
Industrial Electrician
I would like to know if this is understood code or just good practice based on Art. 514.9. To power a fuel tank, I have always installed a seal off when entering the ground from the building source and at the exiting of the ground at the fuel tank source within 17" of the ground, but I cannot find in the code book where this is a requirement or just a safer practice. Art. 514.9 states either/or but I was sure that I recall that it was necessary for a seal off at both ends of the conduit. A little clarification would be appreciated, thanks.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I believe you may be indirectly, referring to Section 514.8. Article 514 treats, underground wiring slightly differently than most classified locations.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Thanks for your reply. Am I correct about 2 locations having a seal off?
Yes, basically. Section 514.8 treats wiring beneath a classified location as being effectively in a Division 1 location so both ends usually end up needing to be sealed because Section 514,9(A) requires a seal at the dispenser no matter what the “boundary” might be.
 