Hello, Does anyone know of a NEC rule pertaining to the securing of a bonding jumper? My specific question is in regard to the use of a two screw non-metalic cable clamp being required to secure a 4/0 bonding jumper as it entered the side-wall of a UPS cabinet. The bare bonding jumper ran about 6 feet on a cinderblock wall. It started at a grounding bar in the room, then was strapped to the wall about every 12" along it's length until it penetrated the sidewall of the UPS unit where it was terminated on an appropriate size lug. I am aware of the requirement of the need to bond the grounding electrode conductor if run in a metalic conduit. In this installation the 4/0 was passing thru an existing hole in the side of the unit. I was told that the clamp was needed at the side-wall of the unit to prevent arcing if a fault condition were to happen? When you run a grounding electrode conductor lets say on a 200 amp residential service the manufacturer supplies you with a knock out for the GEC and no clamp is required in that situation, I don't see any difference? If I am wrong could someone kindly correct me!
Thanks much, Ed P.