No, and the non-rule used to be one every 100'.Is there an NEC requirement for a pull box every 200' of conduit?
No, and the non-rule used to be one every 100'.![]()
For ease of installation the 100 ft. rule is still followed
Yeah...No code but if you only have a 200' fish tape and your vac is broke.........
What is AARP?:grin:
Steve it ain't electrical and you will find out soon. :grin: Hey I get discounts at Mickey D's....
Uhhh Ken have you signed up yet?![]()
Greg I was just having fun poking at you I'm a member as well. :grin:
Feeling stupid this morning...
Is there an NEC requirement for a pull box every 200' of conduit?
(A little background, I have an engineer who insisted that it is in the NEC but can not give me a reference and I cant find one either.)
he should be fired as an electrical engineer. If he is an other type engineer, he should be not-so politely asked to mind his own #%^$@ business.