E ericselectric New member Location woodbine Md usa Oct 8, 2015 #1 Details: single phase 120/240v generator 153 amps output with a factory installed 175 amp ocpd. How do you size the feeder from the genset to the transfer switch?
Details: single phase 120/240v generator 153 amps output with a factory installed 175 amp ocpd. How do you size the feeder from the genset to the transfer switch?
Smart $ Esteemed Member Location Ohio Oct 8, 2015 #2 The easiest is to size for ampacity based on the 175A ocpd. :roll: Looking at 2/0 cu or 4/0 al, assuming 75/90°-rated wire.
The easiest is to size for ampacity based on the 175A ocpd. :roll: Looking at 2/0 cu or 4/0 al, assuming 75/90°-rated wire.