wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
I somewhat sympathize with that attitude, but I don't think this is a good example of the issue. The minimum safe distance between live parts isn't something a typical electrician has learned through experience--at least I hope not, as that would imply having participated in a number of short circuit and arc over events. Rather it strikes me as something determined through engineering tests, etc.I think you know my philosophy Wayne, that I am vehemently opposed to this nanny state/dumbing down /"brother -in-law proofing" of the code where electricians are becoming mere "installers" and can't make any judgements based on actual conditions in the field to make things work.
Anyway, UL 414 "Meter Sockets" Table 8.1 has the answers. For voltage differences of 300V or less, "parts of opposite polarity" need to be 3/8" apart through air, and 3/4" apart measured over a surface. And if one of the parts is "grounded metal" then it's 3/8" through air, 1/2" over a surface. Plus there are some footnotes and details that probably need digesting.
I don't know what the typical stud spacing is on a meter socket such as is being discussed, but it sounds like some pretty wide lugs would still comply.
Cheers, Wayne