Hi All, I just signed up, seems like a great forum. I searched/researched for hours (actually days) and can't find the specific answers to these questions,:
1. What type of portable generator, bonded-neutral or free-floating neutral, meets code when tied into a service panel with a interlock?
2. I read where some say a free-floating neutral generator is not UL listed and therefore not allowed.
3. Some say if you break the bonded neutral from the generator frame, you void the UL listing.
4. Some say if you don't break the neutral bond on the frame, and also have the bond at the service panel than you risk current back flow and shock especially during damp weather.
5. Wow, so what type of generator can you connect to an inlet that connects to the service panel with a interlock?
I would think the generator manufactures would make the portable generators with a two position switch, if on the home mode, it would power the 30 or 50amp 4-wire receptacle (Free Floating neutral) and disconnect the power and break the bonded neutral to the 120 GFI's, etc. and if switched to field mode, then it would do the exact opposite. Seems like this would solve the problems but being they don't wire the gensets this way what can be utilized to properly connect to to a service panel with an interlock as mentioned above?
It appears that the interlock connection method has been debated for over a decade and no one ever seems to agree on what is acceptable and what isn't. It seems like a no win scenario...
Thank you!