It is hard to tell from the picture but that ox doesn't look deep enough for 2 pair of 12/2 nm cables.
It is hard to tell from the picture but that ox doesn't look deep enough for 2 pair of 12/2 nm cables.
It looks like an 18 cu. I'm not sure that Carlon even makes one shallower anymore.
Edit to add:
Interesting. I wonder what they mean by the line in the lower left.....
since we do not have an answer from the manufacturer, we have no idea how they have designed their boxes
What I will go on record as saying, is that the thickness of the plastic at the fastening portions of the boxes may be thicker than the walls of the boxes.
I generally have conversations with children who have better sense than to say one's opinion, being different, is not dumb, just a different angle
My past experience, which is more than 25 years with plastic boxes, has proven to me that these boxes do fail, even at the fastening points.
What code section would make this a violation?
Foolishly stepping in::::::::::
I find the discussion interesting, amd, as usual, there is validity on both sides.
I think one aspect of the situation is which hat one wears. Neither the electrcian or the inspector would ever do anything unsafe and both have liability over their heads.
It seems the longer you work the inspection angle, the more you use your basic tool, the NEC. Not to remove "common sense" from the picture, but when the Code states:
III. Construction Specifications
314.43 Nonmetallic Boxes.
Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.
from an inspectors standpoint, your job is to "follow the book". I ask myself "does this violate 314.43?" Seems it would, and if I eneded up in court I'd not have much of an excuse except "it seemed o.k. to me".
I'm sure there is more than 1 way to look at it, but "provison for support" to me would indicate the designed mounting method. Add to that the design is such to prevent contact between conductors and mounting screws and it would seem,IMHO, if you installed screws that contacted the condcutors, you would be in violation.
Subject to damage lets just use a little common sense Yes we all drill holes where we need them and there not but for cripes sake this is crazy!!!![]()
Ones point of view on this certainly will change depending wether your are looking with inspectors eyes or not. It is a violation. The inspectors don't get to decide wich parts of the code they like and wich they don't. Is it an unsafe installation? Not at all. Could you justify not red tagging it in a court room? No lawyer would do any less than roast you for it!!
I took some pics for you today Pierre :grin:
I was doing some bathroom remodel and had to relocate the wiring from a bath bar to two sconces. I cut my holes for my cut in boxes and found a stud set back about 2.25" You can't really tell from the pic that it's set back. It's a double framed plumbing wall with offset studs.
I used my paddle bit to take out another .25" to accomodate my box and used drywall..err....electrical box mounting screws instead of the crappy plastic ears that come on the box.