don_resqcapt19 said:Just a few short years ago, they said this was not a true statement when I and others were telling this to the public.
Don
The American public ?
They don't need to know.
Don
(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
al hildenbrand said:I see an upsurge in the labeling of areas like Office, Study, Workshop, etc. I also note that attics, unfinished basements, garages, sheds, utility rooms, atriums, foyers, vestibules, lounges, home theaters, studios "and similar areas" are not listed.
:smile:
don_resqcapt19 said:Tom,
It is the combination type device that is required to be used 1/1/08. It can either be a breaker or a stand alone device. Also under the 2008 code the AFCI device can be at the first outlet if the branch circuit is run from the panel to the first outlet in metal conduit or cable. My point is that the original proposals to require the AFCI device said that is could provide protection beyond the outlet. This is the type of protection that the combination device is said to provide, but it is not yet on the market as fas as I know.
Don
dnem said:Does the code panel always have to find the most convoluted way of wording things ? . Don?t they realize the interpretation nightmares or don?t they care ?
Panel Meeting Action: Accept in Principle
The panel revised the wording in the recommendation of the comment to read as follows:
“(B) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arcfault circuit interrupter, combination-type, installed to provide protection of the branch circuit.”
Panel Statement: The panel accepts the submitter’s concept of a more limited approach to the expansion of AFCI. The panel has used language that is arranged in a manner that parallels the language in 210.52(A) and has also included hallways and closets to address previous proposals about those areas.
The panel did not accept the submitter’s deletion of the words “supplying outlets,” because it would introduce confusion regarding branch circuits that passed through these areas but did not supply any outlets in the area.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 8 Negative: 4
BROWN, L.: The Panel’s Action to not require AFCI protection only for the receptacles that typically require GFCI protection is backtracking from the Panel’s Actions and Statements shown in the Report on Proposals (ROP). If they felt the entire house should be protected what relevant fire data changed their minds? Please read NAHB’s Comment 2-79. Calling this a “limited approach to the expansion of AFCI” still results in no cost-benefit for society, it just needlessly increases the costs of housing. No jurisdiction should burden its citizens with this unneeded expense.
There was never any fire study or costbenefit study to support installing these devices only for bedrooms in the 1999 NEC. Since then NO data or study has ever been assembled to support the expansion to the whole house. The fact still remains that home buyers in the U. S. will spend approximately 2 BILLION, 130 MILLION, 230 THOUSAND, and 956 DOLLARS per year to cover losses of only $17,720,000. That is a ratio of 119 times the money spent relative to the monetary loss of $17,720,000.
And, that is if the devices work 100 percent of the time. If you break that down by each state, that lack of a cost-benefit becomes apparently clear. All jurisdictions that contemplate adopting the 2008 NEC, especially those jurisdiction that by law must show a cost-benefit in the adoption, are encouraged to look closely at this cost-benefit fact and not adopt the 2008 NEC until all provisions requiring AFCIs is stricken (Section 210.12).
georgestolz said:So, dust off your wallets ...
georgestolz said:So, dust off your wallets or contact your electrical boards, gentlemen.![]()
Edit to add:
Lawrence Brown, CMP-2 member, submitted several proposals (or maybe, the same proposal several times) to get rid of the requirement. I would also like to quote his response to his negative vote to the comment:
BROWN, L.: The Panel?s Action to not require AFCI protection only for the receptacles that typically require GFCI protection is backtracking from the Panel?s Actions and Statements shown in the Report on Proposals (ROP). If they felt the entire house should be protected what relevant fire data changed their minds? Please read NAHB?s Comment 2-79. Calling this a ?limited approach to the expansion of AFCI? still results in no cost-benefit for society, it just needlessly increases the costs of housing. No jurisdiction should burden its citizens with this unneeded expense.
I'll have to thank him for doing the math for me. :grin:The fact still remains that home buyers in the U. S. will spend approximately 2 BILLION, 130 MILLION, 230 THOUSAND, and 956 DOLLARS per year to cover losses of only $17,720,000. That is a ratio of 119 times the money spent relative to the monetary loss of $17,720,000.
I am not taking sides on this topic, just providing some info I know about.