- Illinois
- retired electrician
The following reorganization for the NEC will be discussed at the Correlating Committee Meeting on March 14 &15. (posted in two parts)
| NEW Article | CURRENT article | title |
| 90 | 90 | Introduction |
| Chapter 1: Definitions and General Requirements | ||
| 100 | 100 | Definitions |
| 110 | 110 | Requirements for Electrical Installations |
| 120 | 220 | Load Calculations |
| 130 | 750 | Energy Management Systems |
| 140 | 590 | Temporary Installations |
| Chapter 2: Wiring and Protection for Systems 1000 VAC, 1500 VDC and Below | ||
| 200 | 300 | General Requirements |
| 205 | 310 | Conductors and Cables |
| 206 | 200 | Use and Identification of Grounded Conductors |
| 210 | 210 | Branch Circuits |
| 215 | 215 | Feeders |
| 225 | 225 | Outside Branch Circuits and Feeders |
| 230 | 230 | Services |
| 240 | 240 | Overcurrent Protection |
| 242 | 242 | Overvoltage Protection |
| 250 | 250 | Grounding and Bonding |
| Chapter 3: Wiring and Protection for Systems Over 1000 VAC, 1500 VDC | ||
| 300 | 305 | General Requirements |
| 305 | 315 | Conductors and Cables |
| 306 | Use and Identification of Grounded Conductors | |
| 330 | 235 | Branch, Feeder and Services |
| 335 | 395 | Outdoor Overhead Conductors |
| 340 | 245 | Overcurrent Protection |
| 342 | 242 | Overvoltage Protection |
| 350 | 250 | Grounding and Bonding |
| Chapter 4: Wiring and Protection for Limited Energy Systems | ||
| 400 | Wiring Requirements and Materials | |
| 405 | 722 | Conductors and Cables |
| 406 | Use and Identification of Conductors | |
| 430 | Interior Cabling Systems | |
| 435 | Exterior Cabling Systems | |
| 440 | 724, 725, 726 | Overcurrent Protection |
| 442 | Chapter 8 | Overvoltage Protection |
| 450 | Grounding and Bonding | |
| Chapter 5: Enclosures | ||
| 520 | 312 | Cabinets, Cutout Boxes, and Meter Socket Enclosures |
| 522 | 314 | Outlet, Device, Pull, and Junction Boxes; Fittings; and Hand hole Enclosures |
| Chapter 6: Wire and Cable | ||
| 620 | 320 | Armored Cable: Type AC |
| 622 | 322 | Flat Cable Assemblies: Type FC |
| 624 | 324 | Flat Conductor Cable: Type FCC |
| 626 | 326 | Intergrated Gas Spacer Cable: Type IGS |
| 628 | 330 | Metal-Clad Cable: Type MC |
| 630 | 332 | Mineral-Insulated, Metal-Sheathed Cable: Type MI |
| 632 | 334 | Nonmetallic-Sheathed Cable: Types NM and MNC |
| 634 | 770 | Optical Fiber Cables |
| 636 | 727 | Instrumentation Tray Cable: Type ITC |
| 638 | 336 | Power and Control Tray Cable: Type TC |
| 640 | 337 | Type P Cable |
| 642 | 338 | Service-Entrance Cable: Types SE and USE |
| 644 | 340 | Underground Feeder and Branch-Circuit Cable: Type UF |
| 646 | 400 | Flexible Cords and Flexible Cables |
| 648 | 402 | Fixture Wires |
| Chapter 7: Conduit and Tubing | ||
| 720 | 342 | Intermediate Metal Conduit: Type IMC |
| 722 | 344 | Rigid Metal Conduit: Type RMC |
| 724 | 348 | Flexible Metal Conduit: Type FMC |
| 726 | 350 | Liquidtight Flexible Metal Conduit: Type LMFC |
| 728 | 352 | Rigid Polyvinyl Chloride Conduit: Type PVC |
| 730 | 353 | High Density Polyethylene Conduit: Type HPDE Conduit |
| 732 | 354 | Nonmetallic Underground Conduit with Conductors: Type NUCC |
| 734 | 354 | Reinforced Thermosetting Resin Conduit: Type RTRC |
| 736 | 356 | Liquidtight Flexible Nonmetallic Conduit: Type LFNC |
| 738 | 358 | Electrical Metallic Tubing: Type EMT |
| 740 | 360 | Flexible Metallic Tubing: Type FMT |
| 742 | 362 | Electrical Nonmetallic Tubing: Type ENT |
| Chapter 8: Raceways | ||
| 820 | 366 | Auxiliary Gutters |
| 822 | 372 | Cellular Concrete Floor Raceways |
| 824 | 374 | Cellular Metal Floor Raceways |
| 826 | 376 | Metal Wireways |
| 828 | 378 | Nonmetallic Wireways |
| 830 | 382 | Nonmetallic Extensions |
| 832 | 384 | Strut-Type Channel Raceway |
| 834 | 386 | Surface Metal Raceways |
| 836 | 388 | Surface Nonmetallic Raceways |
| 838 | 390 | Underfloor Raceways |
| 840 | 392 | Cable Trays |
| 842 | 770,800, 805,810,820,830,840 | Raceways for Limited Energy Systems (Communication Raceways) |