P prossetd Member Jan 26, 2009 #1 I am going from an outdoor substation via underground pvc conduit into a building. Is it ok to rigidly connect the conduit to the building? Or, do i need some kind of expansion connection in the conduit to allow for expansion or seismic problems?
I am going from an outdoor substation via underground pvc conduit into a building. Is it ok to rigidly connect the conduit to the building? Or, do i need some kind of expansion connection in the conduit to allow for expansion or seismic problems?
wbalsam1 Senior Member Location Upper Jay, NY Jan 26, 2009 #2 Is your installation subject to frost movement?
raider1 Senior Member Staff member Location Logan, Utah Jan 26, 2009 #3 Take a look at 300.5(J). This section deals with earth movement, due to frost and earth settlement. Chris
Take a look at 300.5(J). This section deals with earth movement, due to frost and earth settlement. Chris
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 26, 2009 #4 you might want to look at 352.44 also. see it applies also.