If I use dual function breakers for all the 120 v circuits will I need to put the GFCI protected stickers on all the devices?
Was it required when it was a gfci device protecting another device
If I use dual function breakers for all the 120 v circuits will I need to put the GFCI protected stickers on all the devices?
No sir. With a GFCI it comes with stickers, no equipment ground GFCI protected outlet.
In the past I have had inspectors tell me all the devices protected need to be labeled.
Now that we use dual function breakers I thought I might have to put a label on something.
Exactly. You jogged my memory and you stated it the same way. On all the devices that need to be protected.I wouldn't think so but they may want stickers on receptacles that are required to be GFCI protected.
I have had to place these stickers on exterior receptacles or on the covers where they could be seen.
Exactly. You jogged my memory and you stated it the same way. On all the devices that need to be protected.
I was thinking about putting a label on the panel that says all 120 v 20 amp 1 pole breakers , GFCI/AFCI protected
MC cable comes with anti-short bushings but you're not required to use them either.![]()
GFCI receptacles come with said stickers, and they may be able to make you use them if the instructions say so - GFCI breakers don't come with those stickers.Probably one of those follow the installation instructions situations in the inspection s eyes and they come with stickers so you should use them I guess.
GFCI receptacles come with said stickers, and they may be able to make you use them if the instructions say so .......
I agree with you, have not read any instructions for any receptacles in a long time so not aware of what they may say.I rather doubt it. That would just be a BS suggestion in the instructions and not part of the instructions that were submitted to UL for its testing and listing.
I agree with you, have not read any instructions for any receptacles in a long time so not aware of what they may say.
I will say I have seen a lot of questionable instructions on things that do contradict general NEC requirements. Seen many things that state not to use on GFCI or AFCI protected circuits :blink: You would think there is no way such instructions are submitted for listing.