Perhaps
It would take two - one for each side of the 120VAC. The alarm contacts go open circuit, so one would have to make up a circuit (interposing relay and power source) to shunt trip a CB and get a shunt trip CB.
The thresholds are pre-set, however one of the settings is 10% (plus or minus) so that is pretty good.
A shunt trip QO 2pole 100A lists for $400. Add $550 for the monitors. Add additional $xx for the control relay/power source.
what is needed here is a ground ring monitor and current probe assuming the ecg and grounding rod are properly in place, the net currenton the grounding jumper will rise at the instant the neutral. opens as the ecg and system neutral bus are interconected at the mains you need to monitor both the ground bus where it ties to the earting electrodes and the system neutral where the utility ties to the system bus. when it is properly operating a groung fault will show up on both bus bars. normal state is 0 amps on the groundbus and line unbalanceamps on the neutral bus. when the neutral fails that amps will try to use the system ground but it will be a hi resisttance path in comparison to the system neutral. both lines willnow be in series across the loads the standard norms for residential service are. L-N min 114V