Well question wire size to breaker size 240.4 the next higher sized brk can be used if conditions permit ?
Heres a example 500 mcm feeder the breaker is a 400 amp from switchboard to dist panel the panel has a 400 amp brk also were using the 2005 code on this job art 310.16 tables shows copper 500 mcm 75c at 380 amps .
Now i could make the wire match with 2 runs of 3/0 ?
In this example should we need to change or should the load on the feeder be the main factor ?
I feel it should be changed to the size wire to match that breaker and not just the load give me input to what you think.
Heres a example 500 mcm feeder the breaker is a 400 amp from switchboard to dist panel the panel has a 400 amp brk also were using the 2005 code on this job art 310.16 tables shows copper 500 mcm 75c at 380 amps .
Now i could make the wire match with 2 runs of 3/0 ?
In this example should we need to change or should the load on the feeder be the main factor ?
I feel it should be changed to the size wire to match that breaker and not just the load give me input to what you think.