S steve225 New member Location Colorado Apr 10, 2003 #1 Is there a minimum seperation by code when power cable and comm. cable are in the same duct bank? Both cables are in their own conduit. Power is 3 phase, comm. is coax.
Is there a minimum seperation by code when power cable and comm. cable are in the same duct bank? Both cables are in their own conduit. Power is 3 phase, comm. is coax.
B bennie Esteemed Member Apr 10, 2003 #2 Re: proximity of power cable to comm. cable A duct bank is where ducks keep their money. NEMA Bulletin No. TCB2 discusses duct arrangements for underground plastic duct. The interior ducts, in a bank, are called dead ducts,(not a pun) The exterior ducts should be used for heat producing cables.