Ok. I'm doing a design for installation for quite a bit of PTAC units into an existing building (hotel). The PTAC unit has a 19.6 MCA (208V single phase). So for example I want to put 15 of these PTAC units on a three phase panel. If I balance the loads (theoretically, of course they all could be on or only 1 could be on) I have 196A on each leg. In regards to 215.2 (1) do I have to size the conductors for 125 percent of this load or not? Basically I don't really know whether the PTAC units will be a continous load or not. Sure, it's safer to size the feeder/OCP for this panel at 196*1.25 = 245A or 250A but is it really required? Can I use a 225A instead? Or even 200A? I know a continuous load is defined as something that runs for 3 hours straight, but as a new EE I've come across many situations where I'm not sure if something runs for 3 hours straight or not. Like I said, the safe thing would be to assume everything might run for 3 hours straight, but that wouldn't be the most efficient design. Also, is there continous factor already figured in the 19.6 MCA as calculated in accordance with the NEC?