RUWired said:John , the way i always understood and was taught at seminars and such, is that if the EGC is put in the raceway, then it needs to be connected to any pull boxes along the way even though the metal raceways provide the path.
Rick
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be spliced or joined within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E).
Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.
The code said that in the 99 code, but no longer says that. Starting with the 02 code, the EGC is only required to be connected to the box if the circuit conductors are spliced within a box, or terminated on equipment within or supported by the box.John , the way i always understood and was taught at seminars and such, is that if the EGC is put in the raceway, then it needs to be connected to any pull boxes along the way even though the metal raceways provide the path.
RUWired said:Don, what article allows that? The exception in 250.148 only applies to iso ground wires.
Rick
How can you not agree? The code wording is clear.I have a hard time agreeing with your inturpetation of that article.
250.134(B) is satisified by the metal raceway.Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be spliced or joined within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E).