I am trying to size a pull box for a new installation. The desire is to run a single 4" EMT to house a feeder to one panel now, and room to feed an additional panel in the future. The largest conductors will be four 250mcm.
I'm looking for the minimum size allowable for the pull box. The feed will be the 4" EMT coming into one end (shorter) wall, and both the present 3" and unknown (2" or 3") future EMTs will come out of one side (longer) wall.
I want to use a 24" long box so it's long enough to straddle past the center knockouts on two panels on 16" centers. I'm thinking a 24" x 12" x 6" box will do, but the NEC sizing seems to indicate a 24" x 18" x 6" box is necessary.
This will hall under the angle-pull rules. They call for 6x the largest opening, so the 24" is necessary anyway, if I'm correct. But, with only a 3" on the side wall (for now), is the 18" adequate? Your opinions are requested, please.