Pull box sizing and 314.28

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I am trying to size a pull box for a new installation. The desire is to run a single 4" EMT to house a feeder to one panel now, and room to feed an additional panel in the future. The largest conductors will be four 250mcm.

I'm looking for the minimum size allowable for the pull box. The feed will be the 4" EMT coming into one end (shorter) wall, and both the present 3" and unknown (2" or 3") future EMTs will come out of one side (longer) wall.

I want to use a 24" long box so it's long enough to straddle past the center knockouts on two panels on 16" centers. I'm thinking a 24" x 12" x 6" box will do, but the NEC sizing seems to indicate a 24" x 18" x 6" box is necessary.

This will hall under the angle-pull rules. They call for 6x the largest opening, so the 24" is necessary anyway, if I'm correct. But, with only a 3" on the side wall (for now), is the 18" adequate? Your opinions are requested, please.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The key may well be the "in the same row" clause. If your 3" is in the same row as the unknown conduits then the 18" would not meet Code. Different row, it would.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As of now, there is no additional conduit, so its not a concern now.

Incoming 4" x 6 = 24"
Outgoing 3" x 6 = 18"

A 24" x 16" box would comply, and be the next guy's problem. :cool:


Now, about the depth. Is 6" enough, or as long as the fittings fit?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is this what you are looking at

enhance



enhance
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is this what you are looking at

1605739811026.png
Yes, the 3" run in this drawing. A 4" coming from the left, and a 3" going out of the bottom. Only the single angle pull.

If anything is ever added, it would come in in the same 4" and leave through a new hole. I'm only concerned with now.

I'm only sizing for what I'm installing. The customer is the GC and builder, and is doing the rest of the wiring himself.

In fact, I'm working under his permit, as a sub, and doing only the service. He's even providing the wire, so I'm happy.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I took a pic of the outside today, after we ran the 4" conduit inside.

Notes:
1. Both conduits originally went through the wall to the upper-left of the 4" elbow, where the brick was patched and painted. I shortened the distance the lower LB sticks out of the switch. And, no, I haven't installed the strut and straps yet.

2. We didn't remove the original work, but we did reuse both LBs and the painted conduit and connectors. We didn't install the 2" run. (I would have used a single piece.) They're using it for temp power, so I have one coupling to put in.

3. The lower LB must be steel. It weighs about five times as much as the other one!

IMG_0475.JPG
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The rules in 314.28 also apply to the LBs. Since you are using smaller conductors than you would normally see in 4", the LBs may be large enough, but you will have to do a calculation as conduit bodies that are marked are marked for "3 size XX conductors" so any time you have more than 3 conductors you have to do the calculations found in the last sentence of 314.28(A)(3).
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Looks like one of the older pulling LBs and may not be marked. Hopefully it is or 314.28 will be a problem.
 

Carultch

Senior Member
Location
Massachusetts
You have to use the actual size of the raceway that has been installed.

Suppose the raceway is oversized, possibly because you are unifying sizes with other unrelated circuits, or possibly because you are using a spare conduit that was sized without your work in mind. Can you cleverly get around this rule, by using reducing fittings to locally reduce its size, and using the reduced size for this calculation?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I will be going back tomorrow. I'll look in them, and take a pic of the pull box we got installed today.

We'll be pulling in four 250 MCMs and a #4.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Suppose the raceway is oversized, possibly because you are unifying sizes with other unrelated circuits, or possibly because you are using a spare conduit that was sized without your work in mind. Can you cleverly get around this rule, by using reducing fittings to locally reduce its size, and using the reduced size for this calculation?
That would be up to your AHJ. I might accept that, but not without looking at the installation.
 