Sorry about that. Since it was already addressed I thought OP had got that. That would be C in this graphic.
To be honest, at this point I am getting unclear as what type of pull OP has.
According to David and Carultch you need to maintain 6X between the conduit entries I don't see that in your graphic.
If you have two 4" and two 2" conduits entering one side of a pullbox and instead of leaving another side like a straight pull or angle pull, they exit out of the top to go up to floors above, how do you size the dimensions of the box in this regard?
I am attempting a 3D pullbox that I'm describing. Does this help?? Still want to confirm if dimension C is considered an angle pull in pullbox example 1.
If no, would example 2 be considered an angle pull?
If I'm reading your sketches correctly, in both cases you are coming in the front and going out the top. You have an angle pull in both cases.
If the back of the box if fixed, then dimension B would be per 314.28(A)(2).
If the bottom of the box is fixed, then dimension C would be per 314.28(A)(2).
If either the back or the bottom of the box is a removable cover, then dim B or dim C (respectively) would be per Table 312.6(A), one wire per terminal.
If either the back or the bottom of the box is a removable cover, then dim B or dim C (respectively) would be per Table 312.6(A), one wire per terminal.
If I'm reading your sketches correctly, in both cases you are coming in the front and going out the top. You have an angle pull in both cases.
If the back of the box if fixed, then dimension B would be per 314.28(A)(2).
If the bottom of the box is fixed, then dimension C would be per 314.28(A)(2).
If either the back or the bottom of the box is a removable cover, then dim B or dim C (respectively) would be per Table 312.6(A), one wire per terminal.
No. If you arrive at 312.6 by way of 314.28(A)(2) Exception, the stipulation therein instructs you to use "the distance required for one wire per terminal".In following the removable cover rule that directs us to 312.6(A), one wire per terminal...the rule changes when conductors in the raceways are run in parallel according to the language of section 312.6(A)...
So if I had 4 conductors run in parallel in the raceway opposite a removable cover, I would refer to the column with 4 at the top to find the required measurement?
Not in 314.28(A)(2) or the title would not be "Angle or U Pulls, or Splices" and the first sentence would not have a clause containing "where angle or U pulls are made".Is a U-pull considered an angle pull?
No. If you arrive at 312.6 by way of 314.28(A)(2) Exception, the stipulation therein instructs you to use "the distance required for one wire per terminal".
Hmmm...OK So if I have a 4inch conduit entering the back of a jbox opposite a removable cover with 8-350mcm conductors, 4-conductors paralleled, the box need only be 5inches deep? That seems tight.