How much power does a cell tower use? IDK.Not a dwelling.
He said it’s a cell tower for T-Mobile, hence the 83% rule won’t apply.
How much power does a cell tower use? IDK.Not a dwelling.
He said it’s a cell tower for T-Mobile, hence the 83% rule won’t apply.
IDK either. I assume he is at the mercy of some job specs though. He could use a reduced neutral, if it's not in the specs and that would help a little.How much power does a cell tower use? IDK.
Not a whole lot, it’s been years since I done one, but they spec a lot of receptacles, and it’s usually fed by a 6-12 or maybe a 24 circuit 100 amp loadcenter. Usually you just run out of space.How much power does a cell tower use? IDK.
200A is prolly a minimum spec. Most sites use way less, it depends on the size of the of the shelter. That's no big deal. The thing that is irritating is 99% of the gear uses batteries and the rectifiers are straight 240V so even if the overall load is 100A or more the only 120V loads are the lights and some convenience receptacles, less the 5A I bet, yet everyone specs a full size neutral.IDK either. I assume he is at the mercy of some job specs though. He could use a reduced neutral, if it's not in the specs and that would help a little.
Three 3/0 through a 2" is not that big a deal.I was hoping to slide by with that one, If I go to 3/0 I definitely need to install bigger conduit and it's going to be a bit@#.
Engineers love:200A is prolly a minimum spec. Most sites use way less, it depends on the size of the of the shelter. That's no big deal. The thing that is irritating is 99% of the gear uses batteries and the rectifiers are straight 240V so even if the overall load is 100A or more the only 120V loads are the lights and some convenience receptacles, less the 5A I bet, yet everyone specs a full size neutral.
I think it's the LBs that are the concern.Three 3/0 through a 2" is not that big a deal.
Maybe from a ticky tack code rule perspective. Most times the six times the diameter rule won't get called when you are using LBs. And if it is the problem then changing the conduit size won't fix that. I think the OP is afraid of the pipe size.I think it's the LBs that are the concern.
The roller type will usually allow slightly larger conductors than the standard LB's.I've got two different threaded LB's in front of me right now. One says (3) 2/0 max, the other days (3) 4/0 max. They are essentially the same size. The 4/0 one is an Appleton malleable iron with thicker walls, but it has rollers on each side.
Yes, they are called “Mogul”, or you can use a 2 1/2” LB with reducing bushings
We retrofitted 40-50 of them years ago, they went from 24 volt equipment to 48 volt. All were 100 amp single phase panels. Seems like they called for 4-30 amp 240 volt twist locks. They were pretty neglected, all the batteries had been shot for quite a while. Put in all new equipment.200A is prolly a minimum spec. Most sites use way less, it depends on the size of the of the shelter. That's no big deal. The thing that is irritating is 99% of the gear uses batteries and the rectifiers are straight 240V so even if the overall load is 100A or more the only 120V loads are the lights and some convenience receptacles, less the 5A I bet, yet everyone specs a full size neutral.
I don't want to fight getting this wire through these condulets.