Is it ok per the NEC to pull some of the cables through a junction box without terminating them? Thanks in advance
Absolutely.Will the NEC allow this?
Thanks.Absolutely.
I appreciate your helpThanks.
300.3(C) Conductors of Different Systems.
(1) 1000 Volts, Nominal, or Less. Conductors of ac and dc
circuits, rated 1000 volts, nominal, or less, shall be permitted to
occupy the same equipment wiring enclosure, cable, or raceway.
All conductors shall have an insulation rating equal to at
least the maximum circuit voltage applied to any conductor
within the enclosure, cable, or raceway.
Yes. 24Vdc circuits with 300V insulation wireI assume that all the conductors are rated the same voltage
How does it not?...those are Article 725 circuits.24vdc instrumentation cables in a J box. The NEC doesn't even apply to that.
-Hal
While you may not need a box, what ever you install is covered by the NEC and all of the rules apply.Well, unless they are Class 1 (which I doubt) you don't even need a J box. If you do use one you are free to do anything you want. (Except mix them with other cables or conductors of Class 1 or power within it.)
-Hal